I think yet another angle you could look at would be using table 402.5 "Allowable Ampacity for Fixture Wires". In this table a #14 has an allowable ampacity of 17 amps. So for the sake of using the arguement that the 14/2 romex was a fixture wire (which I too agree it is in fact branch circuit wiring), then being protected by a 20 amp circuit would still exceed the value in this table thus again flagging a violation. IMHO, this one is just not worth fighting over with the inspector and in the long run you would be far better off just swapping it out.