thomwillecke
Member
- Location
- Menasha, WI, USA
I was flagged at final inspection of a bathroom because the lighting tripped along with the receptacle GFCI test. The entire bathroom is on a 20A GFCI circuit breaker. This is the first time I've had an inspection fail, and I'm looking for advice on how to negotiate/argue/debate with the inspector, as I am 99% certain that my installation is code-compliant. Here is my analysis:
The inspector could quote no code prohibiting the bathroom lighting from being GFCI protected, only referencing the (understandable and logical) inconvenience of being in a dark bathroom should the receptacle be tripped. Do I suck it up and change my installation, or can you provide tips based off experience on how to convince the inspector to pass the install?
Thank you.
210.8(A) - Ground-Fault Circuit-Interrupter Protection for Personnel in Dwelling Units: All 125-volt, single-phase, 15- and 20-ampere receptacles installed in [...] (1) Bathrooms [...] shall have ground-fault circuit-interruptor protection for personnel.
Compliant. All bathroom receptacles are on a branch circuit protected by a GFCI breaker.
210.11(C)(3) - Branch Circuits Required in Dwelling Units, Bathroom Branch Circuits: In addition to the number of branch circuits required by other parts of this section, at least one 120-volt, 20-ampere branch circuit shall be provided to supply a bathroom receptacle outlet(s). Such circuits shall have no other outlets. EXCEPTION: Where the 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with 210.23(A)(1) and (A)(2).
210.23(A)(1) - Cord-and-Plug-Connected Equipment Not Fastened In Place: N/A
210.23(A)(2) - Utilization Equipment Fastened in Place: N/A
Compliant. The lighting is permitted to be on the same 20-ampere branch circuit as the required branch circuit for bathroom receptacles because the circuit at no point leaves the bathroom.
210.70(A)(1) - Lighting Outlets Required in Dwelling Unit Habitable Rooms: At least one wall switch-controlled lighting outlet shall be installed in every habitable room and bathroom.
Compliant. There is a vanity light controlled by a wall switch.
Massachusetts, for example, has amendment "210.70(D): GFCI Protection of Lighting Outlets in All Occupancies: The operation of a single GFCI device shall not deenergize all lighting outlets in a given area."
Neither the village, county, nor state of my installation have such an amendment. The AHJ has adopted the 2011 NEC.
Neither the village, county, nor state of my installation have such an amendment. The AHJ has adopted the 2011 NEC.
The inspector could quote no code prohibiting the bathroom lighting from being GFCI protected, only referencing the (understandable and logical) inconvenience of being in a dark bathroom should the receptacle be tripped. Do I suck it up and change my installation, or can you provide tips based off experience on how to convince the inspector to pass the install?
Thank you.