thomwillecke
- Menasha, WI, USA
I was flagged at final inspection of a bathroom because the lighting tripped along with the receptacle GFCI test. The entire bathroom is on a 20A GFCI circuit breaker. This is the first time I've had an inspection fail, and I'm looking for advice on how to negotiate/argue/debate with the inspector, as I am 99% certain that my installation is code-compliant. Here is my analysis:
The inspector could quote no code prohibiting the bathroom lighting from being GFCI protected, only referencing the (understandable and logical) inconvenience of being in a dark bathroom should the receptacle be tripped. Do I suck it up and change my installation, or can you provide tips based off experience on how to convince the inspector to pass the install?
Thank you.
210.8(A) - Ground-Fault Circuit-Interrupter Protection for Personnel in Dwelling Units: All 125-volt, single-phase, 15- and 20-ampere receptacles installed in [...] (1) Bathrooms [...] shall have ground-fault circuit-interruptor protection for personnel.
Compliant. All bathroom receptacles are on a branch circuit protected by a GFCI breaker.
210.11(C)(3) - Branch Circuits Required in Dwelling Units, Bathroom Branch Circuits: In addition to the number of branch circuits required by other parts of this section, at least one 120-volt, 20-ampere branch circuit shall be provided to supply a bathroom receptacle outlet(s). Such circuits shall have no other outlets. EXCEPTION: Where the 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with 210.23(A)(1) and (A)(2).
210.23(A)(1) - Cord-and-Plug-Connected Equipment Not Fastened In Place: N/A
210.23(A)(2) - Utilization Equipment Fastened in Place: N/A
Compliant. The lighting is permitted to be on the same 20-ampere branch circuit as the required branch circuit for bathroom receptacles because the circuit at no point leaves the bathroom.
210.70(A)(1) - Lighting Outlets Required in Dwelling Unit Habitable Rooms: At least one wall switch-controlled lighting outlet shall be installed in every habitable room and bathroom.
Compliant. There is a vanity light controlled by a wall switch.
Massachusetts, for example, has amendment "210.70(D): GFCI Protection of Lighting Outlets in All Occupancies: The operation of a single GFCI device shall not deenergize all lighting outlets in a given area."
Neither the village, county, nor state of my installation have such an amendment. The AHJ has adopted the 2011 NEC.
Thank you.