- Chapel Hill, NC
- Retired Electrical Contractor
The receptacle can be on the far side of the sink even if it is closer than 3'-- thus the exception. Remember the receptacle must be within 3' of the sink also....
The exception says "Exception: In bathrooms with less than the required zone the receptacle(s) shall be permitted to be installed opposite the bathtub rim or shower stall threshold on the farthest wall within the room."
Can someone find the substantiation for this-- the link. I can't seem to find it at nfpa site
So what was the justification?
..... I just have got all the .... snail mail stopped from them.......
So now we have be concerned that we placed the receptacle as far away as possible from the tub as deemed by the AHJ?
You do know NFPA stands for National Forest Prevention Association, didn't you?
Only when it can't be placed outside the zone mentioned.and at same time still place one within required distance from the basin.