At a campus there is a large parking lot and they want to add 25 EV charging spaces, the EVSE are 12 kW 240 Volt single phase. The question came up if 208V or 277V would be acceptable and the reply was no "all the chargers require 240V" further clarification was that they do not require a neutral "nor any 120V."
There is some LED light poles to add also that can run off anything (120-277), there are no other loads and no building close by.
The site is a primary customer so the utility delivers service at primary voltage and will provide the hi-voltage work from a vault, a separate transformer is required for the EV charging area.
So my question for the group is whats the best transformer configuration for a 240V EVSE site considering losses voltage drop etc?
The only 240V three phase I have worked on is a old very delta, but our suppliers now offer a 240V in a wye in a few configurations some are tailored to VFD's.
Anyone have experience with this what did you choose (or would you choose) and why?
Disclaimer I am not the one selecting this stuff just curious what people are doing around the country.
There is some LED light poles to add also that can run off anything (120-277), there are no other loads and no building close by.
The site is a primary customer so the utility delivers service at primary voltage and will provide the hi-voltage work from a vault, a separate transformer is required for the EV charging area.
So my question for the group is whats the best transformer configuration for a 240V EVSE site considering losses voltage drop etc?
The only 240V three phase I have worked on is a old very delta, but our suppliers now offer a 240V in a wye in a few configurations some are tailored to VFD's.
Anyone have experience with this what did you choose (or would you choose) and why?
Disclaimer I am not the one selecting this stuff just curious what people are doing around the country.