Big Ass Fan disconnecting means

Status
Not open for further replies.
Location
Midlothian Texas
Occupation
Electrical Contractor
Wanted to pick your guys brain on this one. I installed a couple big ass fans (literal brand name) that come with a VFD built onto the fan inside an enclosure, it comes with a L16-20 cord plug 3ph 480. I installed an outlet for the cord end but was stumped with a disconnect requirement, as 430.109 (F) States cord connected motors shall have HP ratings which the L16-20 don’t have to service as disconnect means. But I don’t think 430.109 applies to this as 430.108 “states between point of attachment to the feeder or branch circuit and point of connection to the motor”. The fan is more of an “appliance” or “equipment” so to speak. The wiring between branch to VFD and then motor etc is all internal. So in this installation does anyone think a disconnect would be required (local interpretations aside)? I interpret it as a no.


Sent from my iPhone using Tapatalk
 
How is that different than a disconnect shutting off the power? Just how often it happens?
Are you talking about the input power to the VFD or the output from the VFD to the motor?
 
Are you talking about the input power to the VFD or the output from the VFD to the motor?
according to OP drive is located at the fan. This probably on input power. I installed one of these before, mine we put the drive down low on a wall, but you definitely are not going to unplug anything above that fan while it is running unless you have an access hole from above the ceiling or are able to crawl in open trusses, etc.
 