I find many people struggle with 3 phase power.
Consider PF as 1 for all of this to keep it simple.
My method is to always revert to single phase in calculations.
On rating labels the specified Amps are always per phase. This confuses many I find.
So lets say the current is listed as 10A on a 3 phase motor label.
So if VL-L = 480VAC (System Voltage is always VL-L) then VL-N= 480/1.732 = 277
Thus power per phase is 277x10 = 2770W =2.7kW.
And for the motor with all 3 phases it is 3x2770 = 8310W = 8.3kW
____________________________________________________________
Most of our folks here are experts on this. Can you list anything about 3 phase or other that you find confuses people.
Do any of you have a really good mechanical or fluid or other analogy to help people understand why 3 phase is so superb and why it was the choice across the planet. There could be four, five, even ten phases. Why not???
Also is it accurate to tell a customer that one 3 phase 200A panel is the same (even better) than 3 panels like his one at home with single split phase 200A??? Assume he does not know what an induction motor really means.
Consider PF as 1 for all of this to keep it simple.
My method is to always revert to single phase in calculations.
On rating labels the specified Amps are always per phase. This confuses many I find.
So lets say the current is listed as 10A on a 3 phase motor label.
So if VL-L = 480VAC (System Voltage is always VL-L) then VL-N= 480/1.732 = 277
Thus power per phase is 277x10 = 2770W =2.7kW.
And for the motor with all 3 phases it is 3x2770 = 8310W = 8.3kW
____________________________________________________________
Most of our folks here are experts on this. Can you list anything about 3 phase or other that you find confuses people.
Do any of you have a really good mechanical or fluid or other analogy to help people understand why 3 phase is so superb and why it was the choice across the planet. There could be four, five, even ten phases. Why not???
Also is it accurate to tell a customer that one 3 phase 200A panel is the same (even better) than 3 panels like his one at home with single split phase 200A??? Assume he does not know what an induction motor really means.