Capacitors have inrush current when first put across an A/C voltage as well. Your mentioned capacitor is drawing more current then the motor load it is supplementing, my guess is you have also overcorrected and will have a leading power factor, on this particular circuit anyway, when running.Test results with 350 mfd capacitor.
Capacitor current: 32A
Line Current on Compresssor start amps: 92A (reduced from 120A)
Unfortunately it was a start capacitor, and i couldn't get into the house to see if lights blinked, before it blew.
Need to find a run capacitor.
I tried to say something like that earlier. A capacitor is storage device for DC circuits. For AC circuits it is an impedance, and a place for exchange of apparent power when used to correct power factor. Power factor at locked rotor and power factor at normal running load will not be same, and it will only reduce apparent power. It will have some resistive component to it which is real power, and again the inrush at motor startup is not all reactive power, the real power portion of that current is still going to load down the supply.Do not confuse the one time DC discharge energy from the cap with the reactive current it supplies every cycle.
Transients occur on two time scales, sub-cycle and multi-cycle.140717-1130 EDT
The light flicker is a result of a transient condition (motor turning on). Power factor is a term that that relates to steady state conditions. It is hard to justify the concept of power factor during the occurance of a time varying non-linear transient load change (startup of a motor). Some form of transient analysis is needed.
If the motor draws a high current for 20 cycles, for example, before the rotor movement starts to affect the motor current through induced back EMF, it can be useful to look at the power factor for that 20 cycle period. Whether you use transient analysis or approximate as steady state, the current for one cycle will still consist of resistive, leading and lagging current contributions from the motor and the capacitor.
The problem is the failure to apply dynamic power factor correction (SCR controlled capacitor) to prevent flicker: the capacitor switching by thyristor should be applied in this case. This paper sheds light on the topic:http://www.epcos.com/blob/530844/download/2/pdf-dynamicpfcan105.pdf
Sahib,
Thanks for this interesting article. Years ago I was involved with an investigation of power fuses blowing on robot welding equipment at an auto assembly plant. Using a PQ recording instrument made by Reliable Power Meters (since then I think they were bought out by Fluke) and after weeks of measurements we determined that the random firing of the thyristors in the welding equipment was causing the intermittent blowing of the input fuses to these units. We ended up recommending electrical interlocking be installed between each unit preventing multiple units from firing at the same time. This was implemented and the fuse problems disappeared.
I am wondering if installing these devices by Epcos could have accomplished the same thing.
Do they dim briefly then return to/near same level they previously was? That would be because of voltage drop during the increased demand occuring while your AC unit is starting. The motor is drawing more power during this short time then it is drawing while running, true power factor will have some contribution but the bulk of the draw is still true power. You are only going to see significant lesser effects by reduced voltage starting or other method that will actually reduce power draw while starting.I would characterize the light decrease as dimming, not a flicker, flicker being where the lighting intensity varies over the interval of light instability. The time duration of the light anomoly is less than 1 sec.
The main component of a hard start kit is a capacitor - it's intent is to provide more capacitance in parallel with the existing motor run capacitor - this will result in more starting torque. The motor will start faster, but will still have a high current demand when first energized - which is your problem with the lights dimming. The starting time will decrease - it is possible the starting current will actually increase with the hard start kit. After all power is work/time, speed up the starting time but with same work accomplished means power will go up for that duration as compared to the longer duration for a slower start.I also think it is saying that Static capacitors although can reduce to some extent the flicker, they cannot stop it. Which is also what the others have been saying.
So unless someone thinks it still worth trying, I'm going to save my $50 on run capacitors, and spend my money on a hard start kit which I hope will lessen the flicker (A proven method and won't mess with my warranties). Also, even if the capacitor mitigated the flicker to be unnoticable, I cannot leave the capacitor in the circuit all the time, since this presents another can of worms (overvoltage, capacitor life, unkown effects on electronics). On the test I noticed my Wi Fi stopped and needed to reset the router, and my digital thermostat dispay was showing heating and cooling.
thanks for all the input.
At my house I have a 5 ton, 2 stage scroll compressor condensing unit, and my house lights blink on the unit starting.
Specs are 118 LRA, 230V, 23 FLA.
Lamps are incandescent 130 V.
Measurements at the unit disconnect switch are:
Normal Voltage 246 V
Starting Voltage: 231 V
Starting Amps: 121 A
Running Amps: 10 A (Low Stage)
Starting time: 1 second.
Start is on Low stage.
This is on a 1 year old house and has done this since installed.
There is no issue when the compressor goes from low stage to high stage.
Neutrals have all been checked, Meter, Panelboard, AC unit/disconnect, and are all tight.
If I place a hard start (start assist) kit (Capacitor and Start Relay) on the compressor, will it reduce the line current to the unit, so that my service doesn't see the full compressor start current? If so, any guess at how much less.
This was the OP. What has not been mentioned yet is transformer size, how much other load is connected to it, size and length of supply conductors. My experiences have been you need to address those issues when you are having voltage drop issues. Had a customer with a commercial garage one time that complained whenever the air compressor started the lights dimmed. POCO transformer was maybe a couple hundred feet of conductor away before even hitting the customer's individual lateral that was maybe about 100 feet long. Talked POCO into installing a closer transformer and it made a big difference.
So you have a fairly decent sized source, about 200 feet of conductor, the overhead portion is likely 1/0 at the largest, the underground probably 4/0. I can almost assure you if you cut that distance in half you will see pretty significant result in the amount of light dimming you notice. It is supported just with some of the data from your OP alone, you are throwing an instantaneous current of 121 amps on the system, that is causing voltage to drop about 15 volts, but most of that current diminishes within a second or so. You did not mention running voltage that I am aware of but it is probably within a volt or two of what it was initially. That kind of drop that fast will be noticeable from an incandescent lamp, then it goes 95+% back to where it was just about as fast, which will also be pretty noticeable. If you were to soft start that motor, you would still have a drop of maybe a couple volts from no load to full load, but will be gradual enough it is not noticeable via lamp performance.50KVA, 7 Houses on overhead lateral, my service drop from lateral tap to service is 80ft., lateral distance tap to transformer is 120ft. POCO conductors are aluminum don't know size. POCO not interested in my blinking lights with such small voltage drop.