Wanted to get opinions on how you guys like to bond a #10 equipment grounding conductor in junction boxes and device boxes.
I like what Infinity said, but whether dealing with solid or stranded conductor may make some difference also.Wanted to get opinions on how you guys like to bond a #10 equipment grounding conductor in junction boxes and device boxes.
I use fork spade connectors to connect the #10 to the box. That makes some inspectors get bent out of shape.
For the most part I install an additional pigtail to connect to the device. Otherwise use a self grounding device if the box is tight.
What's their issue with a fork connector? Proper tooling being used?
SceneryDriver
First trick to working with 10AWG is to use stranded. Once you do that life gets better.
First trick to working with 10AWG is to use stranded. Once you do that life gets better.
I have issues with the code on this issue. #10 ground works fine for breakers up to 60 amps. So my #6 cable can use a #10 ground. But my #10 cable cannot use a #12 ground pigtail.. (unless you are me and nobody is looking that close. Nyuck, Nyuck. )
I have issues with the code on this issue. #10 ground works fine for breakers up to 60 amps. So my #6 cable can use a #10 ground. But my #10 cable cannot use a #12 ground pigtail.. (unless you are me and nobody is looking that close. Nyuck, Nyuck. )
I have issues with the code on this issue. #10 ground works fine for breakers up to 60 amps. So my #6 cable can use a #10 ground. But my #10 cable cannot use a #12 ground pigtail.. (unless you are me and nobody is looking that close. Nyuck, Nyuck. )
Yet solid wraps a screw with no problem so I will stick with solid.
Pre-tail the boxes in the shop. pitb trying to do it in the field especially with a deep box.
Im surprised they don't make #10 ground tails...they are all #12
installed in an impact driver or drillOr you can use a nut driver.
Depends on the circumstances. Do you regularly have enough excess conductor at the boxes? Do you have some 12 solid bare readily available - that with some greenies may be fastest with least materials cost, otherwise regardless of what you are using, they cost more if the foreman is installing them then if the apprentice is installing them, assuming the apprentice gets it right the first time.To each their own but imo those ready made tails, much like "greenies", are mainly a gimmick and another largely unnecessary part to be hauled around. You can simply use the excess egc at the boxes for your tails- roughly the same install time and cheaper too.