I'm a GC in the SF Bay Area. We recently completed a kitchen remodel and on the final inspection the building inspector is making us run a bonding wire from the gas line to the hot and cold water lines at the water heater and bring to a nearby subpanel. These are located in the garage near each so its not hard to do. My electrician says it isn't necessary or correct, he says just run it from the cold water to the gas line. My dilemma is I've got to deal with this inspector on other jobs, so I don't really want to go to the mat on this issue so I'll do what he asks. My question is, is this a hazard or is it just a a pointless, yet harmless exercise?
Noticing your on west coast also. I've having let my California License go (for the second time now) effective April 2d this month. So might not be bad idea to check if "Cali" having amendment to 250.104(B) because greater State of Washington has..
WAC 296-46-250.104(B) Bonding -Other Metal Piping
(9) For flexible metal gas piping installed in new or extended from a existing ridged metal piping system, either:
(a) Provide a copy of the manufacturers bonding instructions to the inspector @ the time of inspection and follow those instructions: or
(b) The bond conductor for the gas system must:
(i) Be a minimum 6 AWG copper; and
(ii) Terminate at:
(A) An accessible location at the gas meter end of the piping system on either a solid iron gas piping fitting using a listed grounding connector;
and
(B) Either the Service equipment enclosure, service grounding electrode conductor or electrode, or neutral conductor bus in the service enclosure.