I'm a GC in the SF Bay Area. We recently completed a kitchen remodel and on the final inspection the building inspector is making us run a bonding wire from the gas line to the hot and cold water lines at the water heater and bring to a nearby subpanel. These are located in the garage near each so its not hard to do. My electrician says it isn't necessary or correct, he says just run it from the cold water to the gas line. My dilemma is I've got to deal with this inspector on other jobs, so I don't really want to go to the mat on this issue so I'll do what he asks. My question is, is this a hazard or is it just a a pointless, yet harmless exercise?
Redundant and useless if the water pipes are already bonded but as long as everything ultimately leads to the main panel via the sub panel ground bus/sub panel ground wire/main panel ground bus where it ultimately gets bonded to neutral and out to a ground rod, I can’t see how it could be hazardous. The inspector should study up on bonding though.