- Location
- Windsor, CO NEC: 2017
- Occupation
- Hospital Master Electrician
If I have an A/C disconnect for a 480v air conditioner, do I need a bonding bushing on the EMT serving it when entering through a concentric knockout?
I agree, see 250.97 and it's exceptions but, per UL you could also remove all the concentric rings and just use reducing washers and eliminate the need for a bushing.Yes unless you are using the maximum size of your concentric knockout.
What is a typical A/C disconnect called by the UL? The closest thing I can find in the white book is "cutout box." Is that right?
Metal reducing washers are considered suitable for grounding for use inknockouts being removed.
circuits over and under 250 V and where installed in accordance with
ANSI/NFPA 70, ??National Electrical Code.?? Reducing washers are intended
for use with metal enclosures having a minimum thickness of 0.053 in. for
non-service conductors only. Reducing washers may be installed in enclosures
provided with concentric or eccentric knockouts, only after all of the
concentric and eccentric rings have been removed. However, those enclosures
containing concentric and eccentric knockouts that have been Listed
for bonding purposes may be used with reducing washers without all
Yeah, I know.George, they would be under "Switches" but that was not what I was refering to, my comment was refering to UL's testing of reducing washers.
(B) Method of Bonding at the Service. Bonding jumpers meeting the requirements of this article shall be used around impaired connections, such as reducing washers or oversized, concentric, or eccentric knockouts. Standard locknuts or bushings shall not be the only means for the bonding required by this section but shall be permitted to be installed to make a mechanical connection of the raceway(s).
Electrical continuity at service equipment, service raceways, and service conductor enclosures shall be ensured by one of the following methods:
(1) Bonding equipment to the grounded service conductor in a manner provided in 250.8
(2) Connections utilizing threaded couplings or threaded hubs on enclosures if made up wrenchtight
(3) Threadless couplings and connectors if made up tight for metal raceways and metal-clad cables
(4) Other listed devices, such as bonding-type locknuts, bushings, or bushings with bonding jumpers
In the event that you are using the concentric, you wouldn't be using a reducing washer.George I read 250.97 except 3 as referring to fittings other than reducing washers.
I don't see any evidence of that in the previously linked to pages, or DWTT.I am thinking there are fittings (connectors) that have a shoulder that somehow touches the box and does not rely on the rings.
But George's question is not pertaining to bonding services. Service bonding has it's own set of rules.250.97 takes us to 250.92(B) except B(1). The highlighted section is brand new to 2011.
But George's question is not pertaining to bonding services. Service bonding has it's own set of rules.
Roger
No, you're right - but as soon as you make use of the exception, then you don't have to make that jump anymore.No but 250.97 sends us to 250.92. .97 says we must use one of the methods specified for services in 250.92. I don't believe it is saying if it is a service use 250.92 but rather you use the same rules. Maybe I am wrong.
Oooops, I was reading right past your reference to 250.97 and was stuck on 250.92.No but 250.97 sends us to 250.92. .97 says we must use one of the methods specified for services in 250.92. I don't believe it is saying if it is a service use 250.92 but rather you use the same rules. Maybe I am wrong.
I will try and forgive you.Oooops, I was reading right past your reference to 250.97 and was stuck on 250.92.![]()
Roger