Okay, I just got ahold of the locality inspector.
He stated that only one end of the CSST needs to be bonded to the electrical electrode system, not both ends. He basically said that the existence of the CSST is what triggers the requirement to bond the main gas line.
I was thinking that running a conductor in parallel with the CSST was best, effectively bypassing it, but he agreed that the solenoid valve's EGC would suffice for bonding that end of it, so we'll be bonding the main line.
He also said a #6 was adequate, and even preferred a bare conductor, so I'll use the #6 solid that we usually use for driven electrodes. Thanx for all of the input, guys. We'll now return you to the regularly scheduled program.