Re: Bonding gas pipe to new residential service
Water pipes may be used as a grounding electrode if they are in contact with the soil for 10 ft. Typically the connection to a water pipe is a bonding connection per 250.104 to allow a low impedance path to the service for a fault current return in the event the pipe is energized.
Grounding to gas piping is not allowed by the NEC, the gas meter has had dielectric unions for many years, as the metal gas piping has cathodic protection, the additional metal on the customer side complicates the cathodic proteciton. Also most new gas service lines are now plastic, as well as many of the gas mains are plastic.
Water pipes may be used as a grounding electrode if they are in contact with the soil for 10 ft. Typically the connection to a water pipe is a bonding connection per 250.104 to allow a low impedance path to the service for a fault current return in the event the pipe is energized.
Grounding to gas piping is not allowed by the NEC, the gas meter has had dielectric unions for many years, as the metal gas piping has cathodic protection, the additional metal on the customer side complicates the cathodic proteciton. Also most new gas service lines are now plastic, as well as many of the gas mains are plastic.