Ok, so I failed inspection and the inspector wrote " Bond house side of gas meter-outside to grounding electrode system"
I have #6 GEC that goes from the panel, outside through the Intersystem grounding bridge to two grounding electrodes in the ground 6 feet apart (not concrete-encased).
I am trying to find out if there is a way for me to connect #6 awg from the gas pipe to the grounding electrode via clamp, or do I need to replace the whole #6 GEC and run a continuous length as per 250.64C through the intersystem grounding bridge, 2 electrodes and loop the gas pipe also.
Looking at 250.68C 2014 NEC, it does not say I can use ground rod 250.52A(5).
Grounding electrode conductors and bonding jumpers shall be permitted to be connected at the following locations and used to extend the connections to an electrode(s):
1. water piping 5 feet...
2. metal structural frame of a building...
3. A concrete-encased electrode 250.52A3
I connected the #6 from gas pipe to intersystem bonding bridge, but as I was reading this thread, the IBB is not rated for GEC connection.
http://forums.mikeholt.com/showthread.php?t=166062
I have #6 GEC that goes from the panel, outside through the Intersystem grounding bridge to two grounding electrodes in the ground 6 feet apart (not concrete-encased).
I am trying to find out if there is a way for me to connect #6 awg from the gas pipe to the grounding electrode via clamp, or do I need to replace the whole #6 GEC and run a continuous length as per 250.64C through the intersystem grounding bridge, 2 electrodes and loop the gas pipe also.
Looking at 250.68C 2014 NEC, it does not say I can use ground rod 250.52A(5).
Grounding electrode conductors and bonding jumpers shall be permitted to be connected at the following locations and used to extend the connections to an electrode(s):
1. water piping 5 feet...
2. metal structural frame of a building...
3. A concrete-encased electrode 250.52A3
I connected the #6 from gas pipe to intersystem bonding bridge, but as I was reading this thread, the IBB is not rated for GEC connection.
http://forums.mikeholt.com/showthread.php?t=166062