I see.
I am trying to find out if there is a way for me to connect #6 awg from the gas pipe to the grounding electrode via clamp, or do I need to replace the whole #6 GEC and run a continuous length as per 250.64C through the intersystem grounding bridge, 2 electrodes and loop the gas pipe also.
Looking at 250.68C 2014 NEC, it does not say I can use ground rod 250.52A(5).
Grounding electrode conductors and bonding jumpers shall be permitted to be connected at the following locations and used to extend the connections to an electrode(s):
1. water piping 5 feet...
2. metal structural frame of a building...
3. A concrete-encased electrode 250.52A3
I connected the #6 from gas pipe to intersystem bonding bridge, but as I was reading this thread, the IBB is not rated for GEC connection.
http://forums.mikeholt.com/showthread.php?t=166062
Do they know how to use a screwdriver?That seems like a reasonable method to get the gas pipe bonded for the plumber.
Ok, so I failed inspection and the inspector wrote " Bond house side of gas meter-outside to grounding electrode system"
I have #6 GEC that goes from the panel, outside through the Intersystem grounding bridge to two grounding electrodes in the ground 6 feet apart (not concrete-encased).
I am trying to find out if there is a way for me to connect #6 awg from the gas pipe to the grounding electrode via clamp, or do I need to replace the whole #6 GEC and run a continuous length as per 250.64C through the intersystem grounding bridge, 2 electrodes and loop the gas pipe also.
Looking at 250.68C 2014 NEC, it does not say I can use ground rod 250.52A(5).
Grounding electrode conductors and bonding jumpers shall be permitted to be connected at the following locations and used to extend the connections to an electrode(s):
1. water piping 5 feet...
2. metal structural frame of a building...
3. A concrete-encased electrode 250.52A3
I connected the #6 from gas pipe to intersystem bonding bridge, but as I was reading this thread, the IBB is not rated for GEC connection.
http://forums.mikeholt.com/showthread.php?t=166062
TrueThe conductor between the gas pipe and the grounding electrode system is not a Grounding Electrode Conductor, so it is not required to be continuous.
Electrical inspector is failing me for it so I have to do it, and I wont get paid for it.That seems like a reasonable method to get the gas pipe bonded for the plumber
Good reference material, thanksG2411.1 (310.1) Pipe and tubing other than CSST. Each above-ground portion of a gas piping system other than corrugated stainless steel tubing (CSST), that is likely to become energized shall be electrically continuous and bonded to an effective ground-fault current path. Gas piping, other than CSST, shall be considered to be bonded where it is connected to appliances that are connected to the equipment grounding conductor of the circuit supplying that appliance.
G2411.1.1 (310.1.1) CSST. Corrugated stainless steel tubing (CSST) gas piping systems shall be bonded to the electrical service grounding electrode system at the point where the gas service enters the building. The bonding jumper shall be not smaller than 6 AWG copper wire or equivalent.
However, I would like to add a comment on the "intersystem grounding bridge" you are referring too. Since I can only assume here you are speaking of the the "Intersystem Bonding Termination" point as required by 250.94 and as defined in Article 100, for use with bonding "communication systems", I would not permit the connection of the CSST bonding/grounding conductor (as specified by the Manufacturer and/or IRC and IGCC) to this device. It is not listed for it nor to the best of my knowledge evaluated for it. While a termination is a termination, liability is assumed by whom ever terminates the bond/ground conductor improperly.
Rick I seem to see an issue with what you posted. It says you can put a bonding jumper to the nearest water pipe yet it also says the bond must be done at the point where the pipe enters the building[/QUOTE
I think I'm not making myself clear. I was only speaking about gas piping not water piping though you could attach to the first 5' of a metal water pipe that was a grounding electrode.
Generally we accept just inside or outside the building. The 2012 IFGC and IRC allow the bond to be between the point of delivery and the first CSST fitting.So you are not of the thinking that the connection must be made outside the building at the entrance to the structure.