The fuse on the blade switch for SFD or small commercial service will. I've been witness to it a couple times.Are you sure about that?
That would be odd, the primary fuse is generally sized to protect the grid not the transformer.
In the link below the secondary short kept going for 30 to 45 minutes until the transformer internal shorted and opened the primary cutout.
http://www.electrical-contractor.ne...p/topics/119389/4_RMC_vs_Utility_Current.html
Your pics remind me of an incident my boss was involved in- 480V phase to phase fault that reset the recloser at the sub station three times and shot fire out of the safety switch every time.