It wouldn't necessarily, but at least hypothetically it could. Suppose my setup is weatherhead > RMC > CT cabinet with isolated neutral bar > more RMC > service equipment. If I use bonding locknuts on the CT cabinet and service equipment, and I don't have concentrics or eccentrics, then the requirements of 250.92 are met without bonding the CT cabinet directly to neutral. So then I don't have a parallel path on the RMC.
And I only said parallel paths on service enclosures and raceways. Ground is still a parallel path, however theoretical or not.