Bonding neutral and ground at service end box in NYC

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
I wanted to say that, but it's actually not in the definition (unless it's changed after the 2017). The definition says "....at the service", and the definition of "service" isn't restrictive to just the service disconnect, as I read it.
Okay it's not in the definition, but it *is* in 250.24(B).
 

gene6

Senior Member
Location
NY
Occupation
Electrician
I can't think of a time where Con-Ed sealed their service end box.
I am talking about a Con ED service end box in a typical NYC basement, these boxes are installed before the meter to separate the service lateral from the service entrance conductors, are we talking about the same box? They are required to be sealed, because they are before the meter.
See blue book section L 'seals' https://www.coned.com/-/media/files/coned/documents/es/specs/electricbluebook.pdf

In this photo above the meters is the con-ed box, note the seals on the meter and the end box:
 

Attachments

  • 115.png
    115.png
    1,022.9 KB · Views: 12
Last edited:

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
I am talking about a Con ED service end box in a typical NYC basement, these boxes are installed before the meter to separate the service lateral from the service entrance conductors, are we talking about the same box? They are required to be sealed, because they are before the meter.
See blue book section L 'seals' https://www.coned.com/-/media/files/coned/documents/es/specs/electricbluebook.pdf

In this photo above the meters is the con-ed box, note the seals on the meter and the end box:
I'm talking about EO-9072-B or EO-9073-B boxes
 
I am talking about a Con ED service end box in a typical NYC basement, these boxes are installed before the meter to separate the service lateral from the service entrance conductors, are we talking about the same box? They are required to be sealed, because they are before the meter.
See blue book section L 'seals' https://www.coned.com/-/media/files/coned/documents/es/specs/electricbluebook.pdf

In this photo above the meters is the con-ed box, note the seals on the meter and the end box:
Yeah I would be surprised if Con ed didn't seal the end box, unless there was metering before it.
 
Top