Bonding question
Mark @ Ampol
New member
Queens NY
Does the code require for switches to be bonded to the box with a bonding jumper (bare or green wire)? This is in New York City, where we use Armored Cable and steel boxes. This is regarding residential wiring.
Thanks,
Mark
It depends on what you are using. MC may be used. Look at 250.118 (10)of the NEC. The old style ac (BX) was not legal as an equipment ground.
Thanks,
Mark
If you're talking about typical wall switch, no. Metal box, metal screws. Box is required to be grounded. Metal switch yoke grounded to box through metal screws.
I agree, the 6-32 screws are all that you need.
Hate to nit pick, but I can't resist. It's not 6 32nds of an inch. The 6 relates to the diameter of the screw. The 32 indicates 32 threads per inch.
You're not nitpicking at all. You're correct the " should not have been in that post so I'll remove it.
Here in Shelby Co. TN, Unless the yoke of the switch makes full contact with a metal box which IS bonded, then the ground wire must be attached to the switch grounding screw. Same with receptacle outlets.
404.9(B) does not address what I stated so it must be a local thing?
The switch and receptacle requirements are different. The NEC does not require direct contact between the switch yoke and the metal box.
Only because you are a moderator and can do so, rest of us have limited time to make changes:p
That is my take on it, but I have an inspector that wants to see the retaining fiber washers removed from all device screws if there is no separate bonding jumper installed.
Mod's will be happy to make edits to a post, all you need to do is ask. :cool:
That's either due to a local thing or a misapplication of the NEC. :D