I am doing an install for 24vac HVAC controls in a northern territory. Class 2 100va. Inspector requested pipe sleeves in wall to protect free air wire, we did this and now he is requesting we bond each one. I bonded each with 14awg to the nearest electrical box but now they are asking for them all to be daisy chained with 10awg bond and then connected to a nearby electrical JB. I also am wiring valves and actuators, typically we install 1110 on duct and do joints in here but I am afraid the inspector is going to make us bond these boxes with 10awg as well... Is there any section of the code that makes me exempt from this. Never had this problem at home. Thanks!
My CEC book is a bit out of date (2018) but from what I recall of Class 2 work in Canada is Rule 12-000 exempts Class 2 wiring methods of Section 12, it does not exempt you from Section 10.
Section 16 generally allows for more flexible wiring methods, but Rule 16-212 emphasizes that Class 2 conductors must be separated from other circuits. If they are installed in a metal raceway, that raceway becomes part of the electrical system's non-current-carrying metalwork and must be bonded per section 10. Then Rules 10-600, 10-606, 10-608 start to kick in, So generally rule 10 requires that the bonding continuity of metal raceways be assured regardless of whats in the raceway, or thats how its been read in the past.
So then your at Rule 10-614 (Size of Bonding Conductor): This is the rule for sizing. It directs you to Table 16 and your #14 should be fine
However Rule 10-116(1): Requires that the conductor be installed such that it is protected from mechanical injury so depending how you run it, the inspector may think #10 is more durable for some reason.
I don't think the inspector can require a #10 but he can require mechanical protection if the #14 is subject to physical damage, you could sleeve the #14 or make sure its protected.
I dont know about the location or environment if say its a plenum / hazardous location over 1000V near by ? So there may be other factors specific to your site triggering obscure rules.
I ran into similar situations doing hazardous location work where class 2 and IS sensors wires were run in underground PVC then switched to rigid metal conduit before they went above ground to a seal off, we pulled a #14 ground wire with the cables to bond the metal junction boxes after the seal off bonding the rest of the non-current-carrying metalwork.