Transformer secondary only needs a GEC to the building steel.
But the indoor panel would be bonded to the building steel as well.Transformer secondary only needs a GEC to the building steel.
The ground rod for the service entrance, connected to the panel. Meter base etc.Yes, but no ground rod needed.
Well it would depend on which electrodes are available. If it has a CEE, no rods would be needed. Yes of course rods are usually the go to electrodes if something needs to be installed like in an existing building where there is no UFERThe ground rod for the service entrance, connected to the panel. Meter base etc.
Right. I land a rod anyway. Can't hurt.Well it would depend on which electrodes are available. If it has a CEE, no rods would be needed. Yes of course rods are usually the go to electrodes if something needs to be installed like in an existing building where there is no UFER
Yup. That's the case in Missouri. PEX water main = 2 ground rods in some counties.Our POCOs require a rod at the meter regardless of any other grounding
Yup. That's the case in Missouri. PEX water main = 2 ground rods in some counties.