Hello
Had a debate about the correct way to wire a transformer, hoping for some help. We have a 480V 3ph 4W panel feeding a 480V to 240V delta wye transformer. From the transformer, we are feeding a 3-phase enclosed circuit breaker, which is feeding a CNC machine. The panel is fed with a neutral, but there is no neutral being used anywhere in this particular feed. We have ground wires coming from the ground bus in the panel to the transformer, going out from the transformer to the ground lugs at the ECB, and from the ECB to the machine. There is also a ground wire ran from the transformer to building steel. All grounds are connected to ground bushings at each end of every conduit, and are connected to a factory installed ground bus inside of the transformer itself.
The question is whether or not we also need to connect the transformer ground bus to the XO.
Thank you very much for any help you can offer
Mike.
Had a debate about the correct way to wire a transformer, hoping for some help. We have a 480V 3ph 4W panel feeding a 480V to 240V delta wye transformer. From the transformer, we are feeding a 3-phase enclosed circuit breaker, which is feeding a CNC machine. The panel is fed with a neutral, but there is no neutral being used anywhere in this particular feed. We have ground wires coming from the ground bus in the panel to the transformer, going out from the transformer to the ground lugs at the ECB, and from the ECB to the machine. There is also a ground wire ran from the transformer to building steel. All grounds are connected to ground bushings at each end of every conduit, and are connected to a factory installed ground bus inside of the transformer itself.
The question is whether or not we also need to connect the transformer ground bus to the XO.
Thank you very much for any help you can offer
Mike.