Re: BONDING
no to the 2 replies, both roger and iwire. I used the section to point out that the NEC does not consider bonding jumpers in the same conduit as the service entrance conductors (which includes the neutral when supplied) as a parallel to the neutral service entrance conductor. There is no exception or dissalowance for the neutral installation detail. The bonding wire is referred to as a jumper.
I also did not say that the use of the neutral as bond was against the code. If you actually read my first post, I said it was not the best way to do it for the reasons I stated. imho
The constraints against parallel conductors does not appear in the bonding and grounding section, but in 300, the conductors.
I am only stating my opinion that I think that the use of the neutral as bond (in this situation) is allowed, not required as it is a lesser quality of install. I think you are both defending your preference.
I would allow the mentioned install and I would allow the bonding jumper.
I would respond to the post in detail but it seems there was no intent to actually understand what i said, only to dispute it out of context.
I am not alone in this viewpoint.
if you have the handbook to the 99 NEC (many have not yet adopted the 2002NEC) the iilustration at 250.11 points out that a bonding jumper from the ko to the neutral is often required, irregardless of whether the neutral was bare and a conductor from the same point by contact, and that would definitely be a sizing problem if you wereto consider that a paralleled neutral. This is no different than bonding the meter case.
paul
no to the 2 replies, both roger and iwire. I used the section to point out that the NEC does not consider bonding jumpers in the same conduit as the service entrance conductors (which includes the neutral when supplied) as a parallel to the neutral service entrance conductor. There is no exception or dissalowance for the neutral installation detail. The bonding wire is referred to as a jumper.
I also did not say that the use of the neutral as bond was against the code. If you actually read my first post, I said it was not the best way to do it for the reasons I stated. imho
The constraints against parallel conductors does not appear in the bonding and grounding section, but in 300, the conductors.
I am only stating my opinion that I think that the use of the neutral as bond (in this situation) is allowed, not required as it is a lesser quality of install. I think you are both defending your preference.
I would allow the mentioned install and I would allow the bonding jumper.
I would respond to the post in detail but it seems there was no intent to actually understand what i said, only to dispute it out of context.
I am not alone in this viewpoint.
if you have the handbook to the 99 NEC (many have not yet adopted the 2002NEC) the iilustration at 250.11 points out that a bonding jumper from the ko to the neutral is often required, irregardless of whether the neutral was bare and a conductor from the same point by contact, and that would definitely be a sizing problem if you wereto consider that a paralleled neutral. This is no different than bonding the meter case.
paul