Re: BONDING
With PVC or SE used between the service panel and the meter socket a bonding wire is pointless and a violation of 310.4.
If you run a metallic conduit between the service panel and the meter socket and that conduit basically becomes a neutral conductor as shown in Eds drawing.
The code will not allow this between a SDS source and the first disconnect.
Also the code will not allow this between two structures.
To me it is an oddity that this is allowed (metallic conduit) between two bonded enclosures.
Darn right.Originally posted by websparky:
The code permits the grounded conductor to be bonded to the meter can even if there is a metalic connection via conduit between it and the service disconnect, right?
Yes and no, this thread keeps drifting around but look back far enough this was about requiring a bond wire between a meter and a service panel when there is PVC or SE between them.Originally posted by websparky:
However, you are pointing out that if this is the case, you will have a parallel path for "neutral" and "fault" current, right?
With PVC or SE used between the service panel and the meter socket a bonding wire is pointless and a violation of 310.4.
If you run a metallic conduit between the service panel and the meter socket and that conduit basically becomes a neutral conductor as shown in Eds drawing.
The code will not allow this between a SDS source and the first disconnect.
Also the code will not allow this between two structures.
To me it is an oddity that this is allowed (metallic conduit) between two bonded enclosures.