Boom
chris kennedy
Miami Fla.
Retired electrician
Went to a service call today. The full size 2 pole in positions 5 and 7 was tripped. Feeds a small sub-panel below this one. I took it out to inspect the breaker and buss. All looked OK so I began to put it back. As I pushed it in the insulator between C and B buss failed and BOOM, out go the lights. I took a piece of THHN insulation from a 350 and slipped it between the busses to get the business open for today.
Also, that black 12 connected to the neutral bar, that used to be a neutral.:roll:
Is this one of those General D or Square Electric panels I keep hearing about?
I don't see a main, so this must be a subpanel itself. Noodle bar isn't bonded, so where do all the green wires go?????
Glad you didn't get hurt. I worked in a pool room where there was a panel for the pumps. The chlorine had corroded much of the cover. I was helping a fellow EC who was adding a DP breaker to the panel. The easiest spot to install the breaker was down at the bottom. I noticed the buss was corroded so I installed it at the top of the panel. My friend, who has poor vision, went to hook it up but didn't like where I installed it so he moved it. I was outside and I heard this bang and I immediately realized what happened. My friend came running out and nearly jumped in the pool because his hand got burned so badly. He was very fortunate.
How's this for a BOOM !
Thank God no one was hurt! I wasn't in the yard that day but 2 of my co-workers were. Had it been 10minutes later, they would have been standing right by that tank!!!!
See the transformer in the background? That blew last year!
I swear, I'm bringing in some holy water to sprinkle around that yard!
No one has asked about what PPE you were wearing.(I'm certain this is a mere oversight and not an indication of what a bunch of heartless SOB's we all are!) Glad you were not hurt.A very good reminder to us all that we need to be carefull every single moment!!And I think I speak for all us when I say I am very happy to hear Al wasn't hurt!!:D:D