boost xfmr wire size

Status
Not open for further replies.

Smart $

Esteemed Member
Location
Ohio
I am fairly certain the OP is talking about the factory installed leads on the buck boost transformers.
Ah! That makes sense.

NEC does not have direct purview on the leads as they are part of an assembly that is UL listed. They probably have high-temp rated insulation and, as Ingenieur mentioned, a much higher ampacity rating than the common building wire the NEC deals with.
 
I am fairly certain the OP is talking about the factory installed leads on the buck boost transformers.

That is correct. They are 1.5 kva transfomers with approriate leads for isolation transformer duty, but we are using them for boosting the voltage from 208v to 222v for a total 36kva motor load.
 
Ah! That makes sense.

NEC does not have direct purview on the leads as they are part of an assembly that is UL listed. They probably have high-temp rated insulation and, as Ingenieur mentioned, a much higher ampacity rating than the common building wire the NEC deals with.

That makes sense. Thank you.
 