Dennis -
I rarely ever get involved in house wiring issues - I'm not in the house wiring business.
However, a similar issue occasionally comes up on derating conductors in short nipples. Between 310.15.A.2 Exception, and 310.15.B.2 the short nipples generally don't matter.
I see now that the discussion appears to center on the NM cables laying on each other between the studs. And my thought, as you said, doesn't apply.
Mike -
I reread section 310.15.A several times. Didn't see any mention of "different ambient temperatures". However, I believe you that it doesn't apply to this discussion.
I now recall some of the reasons I don't get involved in house wiring discussions.
carl
I rarely ever get involved in house wiring issues - I'm not in the house wiring business.
However, a similar issue occasionally comes up on derating conductors in short nipples. Between 310.15.A.2 Exception, and 310.15.B.2 the short nipples generally don't matter.
I see now that the discussion appears to center on the NM cables laying on each other between the studs. And my thought, as you said, doesn't apply.
Mike -
I reread section 310.15.A several times. Didn't see any mention of "different ambient temperatures". However, I believe you that it doesn't apply to this discussion.
I now recall some of the reasons I don't get involved in house wiring discussions.
carl