If it's on the bottom you can get away with locknuts.
Is that in the NEC for a pull box?
If it's on the bottom you can get away with locknuts.
FS or FD box yes. But those are not knockouts, those are integral hubs.
What box/enclosure/cabinet are we talking about?
Always thought hub was the ones that stick out of the box like this. Guess intergral mean within.
Is that in the NEC for a pull box?
Alos, so why is it sometimes I see RGS connected into a box with a fitting as you see and sometimes(with the same box) there is no fitting and just the end of the conduit going in. My guess is if they have to cut the conduit then instead of threading the conduit they just attach the fitting. Ding Ding Ding????
Correct.
Ok last question. So are those fittings pictured different than meyers hubs? If so what's the difference between the two? Thanks
314.15 says to prevent moisture from entering. Therefore, I will use "Myers" hub on top.
314.15 says to prevent moisture from accumulating. Therefore, I will use standard locknuts (or the "no-thread" connector mrlucky posted) on bottom.
Two things.
The myers hub is for threaded entry only and can be used anywhere on entering the enclosure.
It also has a sealing gasket.
The pic you posted is a compression fitting, no threads, and assuming that it is rated for a wet location could be used if entering below live parts. If above live parts one could possibly use such a fitting and and a sealing auxiliary fitting, seal ring or seal lock nut, I have from the sides but never at a top penetration.
So the pic with the light......that fitting is not a threaded fitting? Isn't it this fitting which is threaded? I'm confused.
So the pic with the light......that fitting is not a threaded fitting? Isn't it this fitting which is threaded? I'm confused.
But our drawings call for conduits to enter top and leave bottom.
A NEMA 3R say about 30". Guess it could come with concentric KOs. So I guess they would have to do a field KO and use meyers hub.
So the pic with the light......that fitting is not a threaded fitting? Isn't it this fitting which is threaded? I'm confused.
you've never heard of a threadless connector?
I believe the factory Ko's would be at the bottom of the box and not on the top or sides
Sealing locknuts are intended for RGS/IMC. They are intended to go on the outside of the enclosure so the "seal" is on the exterior side of enclosure.Yes. So if you use a threadless connector and sealing locknuts you will have a watertight seal on the outside of the box where the connector makes contact? Or, I assume that what the sealing locknuts are for.