(2) Clamp Fill. Where one or more internal cable clamps,
whether factory or field supplied, are present in the box, a
single volume allowance in accordance with Table 314.16(B)
shall be made based on the largest conductor present in the
box. No allowance shall be required for a cable connector with
its clamping mechanism outside the box.
A clamp assembly that incorporates a cable termination for
the cable conductors shall be listed and marked for use with
specific nonmetallic boxes. Conductors that originate within
the clamp assembly shall be included in conductor fill calculations
covered in 314.16(B)(1) as though they entered from
outside the box. The clamp assembly shall not require a fill
allowance, but the volume of the portion of the assembly that
remains within the box after installation shall be excluded from
the box volume as marked in 314.16(A)(2).