all the conductors in one conduit and is the pull straight thru or angle ?
 
Its a straight pull.. am trying to eliminate the vault next to the pole the is no need for it and I want to install a 4x4x4 inside the pole for the connection.
4431e14c422bf5e6dccae990da2b07f7.jpg



Sent from my iPhone using Tapatalk
 
No.

Not sure why you want a box if you are terminating in the pole but, that said, a straight thru pull requires a box 8 X the conduit size for conductors #4 and larger so you smallest box would be 8" assuming a 1" conduit
 
What about the open holes on the pole do they need to be seal? I know that was not right there is no need for a vault next to the pole just to have a JB in there.


Sent from my iPhone using Tapatalk
 