Here's the scenario...
I've got six dedicated 20-amp branch circuits, each feeding a receptacle.
Due to space issues, they are all being routed down a wall through a single 1-1/4" EMT conduit.
Please tell me if I'm looking at this correctly.
12 CCC's: derate to 70%.
25A x 0.7 = 17.5A.
Can I use the "next standard size higher" rule to keep the circuit breakers feeding these circuits at 20 amps?
The client insists on 20-amp circuit vs. 15-amp, so it's either this or provide #10's.
I've got six dedicated 20-amp branch circuits, each feeding a receptacle.
Due to space issues, they are all being routed down a wall through a single 1-1/4" EMT conduit.
Please tell me if I'm looking at this correctly.
12 CCC's: derate to 70%.
25A x 0.7 = 17.5A.
Can I use the "next standard size higher" rule to keep the circuit breakers feeding these circuits at 20 amps?
The client insists on 20-amp circuit vs. 15-amp, so it's either this or provide #10's.