How can I be misquoting when I quoted the code directly?:? You will notice that the word "receptacle" is nowhere to be found in "Appliance Branch Circuit" definition. This is a General Purpose Branch Circuit by the definition in the code..
You did
not quote code directly. I say you were misquoting the definition because you
left out the part of the General Purpose Branch circuit definition that specifically distinguishes it from the Appliance Branch Circuit definition. That word is
lighting or luminaires. Just because the word "receptacle" is not in Appliance branch circuit definition does not mean it is limited without one. It is still an "outlet", .
Here are the
2 different definitions specifically.
Appliance Branch Circuit: A branch circuit that supplies energy to one or more outlets to which appliances
are to be connected and that has
no permanently connected luminaires that are not a part of an appliance.
General Purpose Branch circuit: A branch circuit that supplies two or more receptacles or outlets for
lighting and applicances.
The NEC would have not added Appliance Branch circuit definition if every outlet or receptacle was a 'General Purpose'. Remember these outlets were intended specifically for these appliances so it would meet the definition of
Appliance Branch Circuit definition to a tee!. If that was not the intended purpose you may have a basis of argument. I agree with Smart$
Smart$ said:
Doesn't matter. The definition of appliance branch circuit uses the term "outlet". A receptacle is but one form of an outlet.
david luchini said:
This is incorrect. The code applies to the installation of the conductors, raceways and equipment for the premise wiring system. The code is silent as to what the end user may or may not plug into the receptacles.
I know this is an age old debate, on whether the NEC extends beyond the outlet or receptacle and affects the end user. I believe you are incorrect.
The code does speak to the end user in many situations on what may or may not be plug into the receptacles. 2008 NEC 422.51 on vending machines come to mind, or 422.45 or 590 that deals with holiday lights. Another code section is 210.21(B)(2) Total Cord and Plug Connected Load.
Whether the end user knows the NEC or not, this does not change the fact that the NEC applies or has been violated on occassion. You also misquoted 90.2
. Read it again, it is not just limited to premise wiring, it also says in (3) Installations of conductors and equipment that connect to the supply of electricity. No where will you find in the NEC where it says it will NOT apply to the end user or what may be plugged into receptacles.
So when these outlets(receptacles) are intended for coffee pots and toasters that exceed the 20 amp branch circuit, the moment someone plug them in and turn them on and exceed the rating, it is a violation.