You did not quote code directly.
:? In post #22, I quoted...
Branch Circuit, General Purpose: A branch circuit that supplies two or more receptacles or outlets for lighting and appliances.
This is a
DIRECT QUOTE from Article 100 of the Code. I don't know how to be any more clear than that.
The NEC would have not added Appliance Branch circuit definition if every outlet or receptacle was a 'General Purpose'. Remember these outlets were intended specifically for these appliances so it would meet the definition of Appliance Branch Circuit definition to a tee!. If that was not the intended purpose you may have a basis of argument.
By your logic, there would be no such thing as a general purpose branch circuit. If you had a branch circuit in an office space with say 6 receptacles on it that was intended for plugging appliances such as computers and monitors (meeting the definition of general purpose branch circuit) it would cease to be a general purpose branch circuit as soon as an appliance is plugged in?!?! I don't believe that this is what the code intended.
I know this is an age old debate, on whether the NEC extends beyond the outlet or receptacle and affects the end user. I believe you are incorrect. The code does speak to the end user in many situations on what may or may not be plug into the receptacles. 2008 NEC 422.51 on vending machines come to mind, or 422.45 or 590 that deals with holiday lights. Another code section is 210.21(B)(2) Total Cord and Plug Connected Load.
I don't see that at all. 422.51 refers cord-and-plug connected vending machines
requiring a GFCI as an integral part of the attachment plug. 422.45 refers to electrically heated appliances intended to be applied to combustible materials
requiring a Stand. The only thing I see about "holiday lights" in Art. 590 is that they shall be "listed" and not used for more than 90 days. As far as 210.21(B)(2), it only tells you the maximum cord-and-plug connected load that can be connected to any single receptacle, but says nothing about the branch circuit as a whole.
Whether the end user knows the NEC or not, this does not change the fact that the NEC applies or has been violated on occassion.
You seem to be contradicting yourself here. Earlier, you stated that it was a Code violation to
KNOWINGLY exceed the rating of a branch circuit by plugging in appliances with a sum of ratings that exceed the rating of the branch circuit. Now you are saying it is a violation if someone
UNKNOWINGLY does the same.
You also misquoted 90.2
. Read it again, it is not just limited to premise wiring, it also says in (3) Installations of conductors and equipment that connect to the supply of electricity. No where will you find in the NEC where it says it will NOT apply to the end user or what may be plugged into receptacles.
I didn't
QUOTE 90.2 at all, so I'm not sure how I could have
MISQUOTED it. :? But 90.2(3) says Installations of conductors and equipment that connect to
THE SUPPLY of electricity (ie, the source.) The appliances in question do not connect to
THE SUPPLY of electricity, but rather to receptacles outlets on the premise wiring system. You will not find anywhere in the NEC where it says that it DOES apply to what the end user may plug into the receptacles, other the maximum cord-and-plug connected load for any single receptacle or single piece of equipment on a branch circuit per
210.21(B)(2) and
210.23(A)(1). But
Article 210 is
SILENT on the calculation of branch circuit loads. Article 220 covers branch circuit loads.
So when these outlets(receptacles) are intended for coffee pots and toasters that exceed the 20 amp branch circuit, the moment someone plug them in and turn them on and exceed the rating, it is a violation.
Again, this is not correct. 220.10 says branch circuit loads
shall be calculated as shown in...220.14. 220.14(I) says that
RECEPTACLE OUTLETS (which is what you have on your branch circuit) shall be calculated at not less than 180VA per single or multiple multiple receptacle on one yoke. You will find
NOTHING in 220.14 about calculating the load on a branch circuit based on the ratings of the appliances plugged into the receptacle outlets. Zero. Nada. It's simply not there.