Can someone tell me if it's ok per NEC code to run two different branch circuits from different panels in the same conduit to a shared detached garage. I am just not sure, thanks.
225.30 Number of Supplies. A building or other structure
that is served by a branch circuit or feeder on the load side
of a service disconnecting means shall be supplied by only
one feeder or branch circuit unless permitted in 225.30(A)
through (E). For the purpose of this section, a multiwire
branch circuit shall be considered a single circuit.
Where a branch circuit or feeder originates in these additional
buildings or other structures, only one feeder or
branch circuit shall be permitted to supply power back to
the original building or structure, unless permitted in
225.30(A) through (E).
IMO, no . Since the garage is attached then article 225.30 would limit you to one branch circuit or one multiwire branch circuit with a few exceptions
Detached garage.How does article 225 Outside branch circuits and feeders apply to an attached garage?
How does article 225 Outside branch circuits and feeders apply to an attached garage?
Detached garage.
IMO, no . Since the garage is attached then article 225.30 would limit you to one branch circuit or one multiwire branch circuit with a few exceptions
Well that was darn unhandy of him. He had the right code reference, just used the wrong adjective.:slaphead::slaphead::slaphead:
Darn Dennis through me off.:ashamed:
Well that was darn unhandy of him. He had the right code reference, just used the wrong adjective.
So we all agree, you can't feed a Detached Garage from two panels, yes?
For the dwelling unit you cannot run a circuit from one unit's panel through another unit.
Does that apply to the garages too?
I know that is true for service conductors but what article states a branch circuit cannot run thru another unit?
I don't see how running through the second unit is "supplying loads".
I don't see how running through the second unit is "supplying loads".
Exactly.. No loads are being supplied just running the branch circuit thru the unit
i am in particular picturing a dwelling unit basement with branch circuit conductors from one dwelling passing through a basement of another dwelling