We had a contact resistance (micro-ohm) test on an 800 Amp thermal magnetic breaker,with a test current of 10 amp. The results were
Phase
A = 79mOhms (Line to Load) through the closed breaker
B = 115mOhms (Line to Load) through the closed breaker
C = 95 mOhms (Line to Load) through the closed breaker
The manufacturer came back with a recommendation that the breaker be replaced due to the "large variation" in the phase to phase contact resistance. Those seem to be very good values to me and did not realize that variations within the specified "acceptable test range" it cause for concern. Can someone please elaborate?
Phase
A = 79mOhms (Line to Load) through the closed breaker
B = 115mOhms (Line to Load) through the closed breaker
C = 95 mOhms (Line to Load) through the closed breaker
The manufacturer came back with a recommendation that the breaker be replaced due to the "large variation" in the phase to phase contact resistance. Those seem to be very good values to me and did not realize that variations within the specified "acceptable test range" it cause for concern. Can someone please elaborate?