breaker height

Status
Not open for further replies.

ktollar

Member
NEC 404.8A 6'7" breaker height as a switch. The main breaker in a panel, whats the maximum height for mounting?? Will not be switched on or off unless trips or panel needs to have the power turned off!!
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
240.24 provides the same requirement for overcurrent devices in general.
 

iMuse97

Senior Member
Location
Chicagoland
NEC 404.8A 6'7" breaker height as a switch. The main breaker in a panel, whats the maximum height for mounting?? Will not be switched on or off unless trips or panel needs to have the power turned off!!

If someone wanted to use it as a switch (ie. to turn the power off), would that not make it a CB used as a switch?

In my experience and interpretation there are no exceptions to the rule except as listed in 404.8 (A) Exceptions 1, 2, & 3. The point being, that if you need to use it, it is readily accessible.
 

jaylectricity

Senior Member
Location
Massachusetts
Occupation
licensed journeyman electrician
In my experience and interpretation there are no exceptions to the rule except as listed in 404.8 (A) Exceptions 1, 2, & 3. The point being, that if you need to use it, it is readily accessible.

So are there exceptions to the rule, or not? :-? :)
 