zog
Senior Member
- Location
- Charlotte, NC
I remember the time when (working for a testing co) I was racking out a 4000A 480V FPE air frame main breaker from a switchboard with xfmr energized on line side. No PPE back then!! All of a sudden while racking we heard a loud "Clunk", we all looked at each other.....WTF!!
When we got the breaker out we found that the line side phase B Stab (looks like a heavy copper pipe) fell off the back of the breaker (broken weld.) :jawdrop:This is a pole piece that engages the stationary fingers. Had it gone phase to phase on the line side, I would not be telling this story......yeah..!
ask me what I think of FPE...!!
One of these? There are still a lot of these out there in service, we get a lot of them that come in for repairs.