JOHNEO99 said:75 Degree Column
Dennis Alwon said:6/2 romex --60 degree column (all romex uses 60 degree). article 334.80 You can go to the next higher size breaker if the rating is not a standard size breaker. Article 240.4 (B)
Dennis Alwon said:6/2 romex --60 degree column (all romex uses 60 degree). article 334.80 You can go to the next higher size breaker if the rating is not a standard size breaker. Article 240.4 (B)
winnie said:Say you have a 55A conductor. It is okay to put 54A of load on this conductor and protect it with a 60A breaker. It is not okay to put 56A of load on this conductor.
-Jon