Hard wire loads like that should have a separate disconnect which is fused for the unit.What about hard wired loads? Such as an air hanlding unit that only drawing 2 or 3 amps. Is a 15 amp breaker responsible to protect that?
Hard wire loads like that should have a separate disconnect which is fused for the unit.What about hard wired loads? Such as an air hanlding unit that only drawing 2 or 3 amps. Is a 15 amp breaker responsible to protect that?
Usually manufacturers group similar size breakers in categories, called frame sizes. Typical frame sizes I've seen are 60A, 100A, 200A, 300A, 400A, 600A, 800A, 1000A, and 1200A. This means 90% of the ingredients of the breaker are the same for the smaller sizes within the category, such that a 40A and 60A breaker would be mostly the same, and both be considered 60A frame sizes. The essential difference is the calibration of the trip mechanism. E.g. the thermal sensing bimetallic strip, the solenoid, the magnet, etc.So physically a 5 or 10 amp breaker would be different than a 15 amp breaker or higher?
True. It's much more economical to gang-up multiple receptacles and/or light fixtures on the same circuit, and use 20A circuits, instead of just running individual 5A circuits to each light fixture.I'd say the same thing applies to us: it's not economical to place so few outlets on each circuit.
Someone in authority claims that each outlet or receptacle will use 1.5 amps on average. 80 percent of a 15 amp circuit is 12 amps. 12 amps divided by 1.5 amps equals 8 outlets/ receptacles. That's the golden rule.
I don't see how Larry criticised you. Most of us on here are very picky about answers being 100% correct. There are some who believe the 180 VA each applies to installations not just calculations, even though the code doesn't say that. Then there are some who just use that as a good common practice rule. I personally do not find it accurate to call that a "golden rule" as I don't find it particularly common. Also just note that even if the 180va applied to installations, there would most times be no 80% derating, that is for continuous loads only.I'm trying to help out the OP since he is hung up on grasping the answer to his questions. why criticize my basic answer to his questions?
I think wiring has everything to do with what I mentioned.
The NEC defines several ampacity ratings for branch circuits, with the minimum being 15. A standard piece of household equipment with a NEMA 5-15P plug may get plugged into a branch circuit with a 15A or 20A overcurrent protection device. It is the equipment manufacturer's responsibility (and something UL will test for) to design their equipment to function safely on such branch circuits. Sometimes, this may involve supplementary overcurrent protection in the equipment itself; e.g., Christmas lights with fuses installed in the plug.In other words, a load that only draws 3.6 amps (for example) would be designed to still be able to handle 15 amps?
This reminds me of people who think using a car battery to jump-start a motorcycle will cause the bike's battery to explode. As long as you're within the designed voltage range, the line current should never exceed the load's demand. The 3.6a load's wiring should never see 15a.In other words, a load that only draws 3.6 amps (for example) would be designed to still be able to handle 15 amps?
It wasn't a criticism, but a clarification.I'm trying to help out the OP since he is hung up on grasping the answer to his questions. why criticize my basic answer to his questions?
The 180va figure is in the load calcs section.I think wiring has everything to do with what I mentioned.
I've tripped breakers too often when my wife and I both wanted to run heating-type appliances at the same time. It is nice to have zones, but it adds cost. You're sizing each circuit for its maximum demand over the year, not its average, much like mini services.Except for SABCs, bathroom receptacles, laundry and some other dedicated circuits, you could put the entire rest of the house on one 15A circuit if you wanted.
-Hal
There is nothing incorrect about what I said. Too bad you don't like the term golden rule.I don't see how Larry criticised you. Most of us on here are very picky about answers being 100% correct. There are some who believe the 180 VA each applies to installations not just calculations, even though the code doesn't say that. Then there are some who just use that as a good common practice rule. I personally do not find it accurate to call that a "golden rule" as I don't find it particularly common. Also just note that even if the 180va applied to installations, there would most times be no 80% derating, that is for continuous loads only.
Are you referring to non-dwelling receptacles? The NEC would apply to nothing you've said when you have a 15 amp dwelling receptacle circuit.Someone in authority claims that each outlet or receptacle will use 1.5 amps on average. 80 percent of a 15 amp circuit is 12 amps. 12 amps divided by 1.5 amps equals 8 outlets/ receptacles. That's the golden rule.
Load calculations are directly related to overcurrent protection. It is called cross-referencing.It wasn't a criticism, but a clarification.
The 180va figure is in the load calcs section.
I know that, and I never would use a 15 amp circuit for SABCs, laundry, or other dedicated circuits. That is a different situation and a different circuit from what I was speaking.Except for SABCs, bathroom receptacles, laundry and some other dedicated circuits, you could put the entire rest of the house on one 15A circuit if you wanted.
-Hal
Yes there was. Even going by 180 VA per recep, you would not take 80% of that . 80% is for continuous loads and 220.14(I) receps are unlikely to be continuous loads. It's a free country and you can use whatever rule of thumb you want, but your implication that your 8 is some standardized industry thing is just not true.There is nothing incorrect about what I said. Too bad you don't like the term golden rule.
Is it really that stressful for you to have a conversation?I will leave it to you guys to do your thing on this forum. I'm too old for this.
It is the equipment manufacturer's responsibility (and something UL will test for) to design their equipment to function safely on such branch circuits. Sometimes, this may involve supplementary overcurrent protection in the equipment itself; e.g., Christmas lights with fuses installed in the plug.
Understood. I like the christmas lights example.It's up to the manufacturer to minimize spontaneous combustion of their products.
I never thought of doing that.This reminds me of people who think using a car battery to jump-start a motorcycle will cause the bike's battery to explode.