... I can only think of 2 things: 1) it's a conductor that's between the panel and the last receptacle that is very slightly damaged somehow, and occasionally arcs or 2) the conductor from the panel to receptacle #2 runs through the crawlspace and might have a junction box that I'm unaware of and there is a loose connection or there is water in the junction box.
Perhaps you could put an in-line slow blow 20A fuse in series with the hot wire in box #2 that's fed from the panel. Or if there's not enough room in box #2 with the GFCI receptacle, in box #3 instead. Then if the the breaker trips but the fuse doesn't blow, it's likely there's a short in the branch circuit upstream of the fuse location (which would be the conductor, etc. in the crawlspace if that conductor is fused in box #2).