I don't think a GFCI breaker will function, as far as the set/reset/test electronics is concerned, without the breaker neutral/pigtail connected. Now if the GFCI breaker had been installed and set, it may work, but I'm not sure it would set without the neutral from the breaker connected. I may be wrong about this.A megger would be a more definitive test of the conductor insulation, etc., but you could also use a GFCI breaker to do some testing. This would be using 120V instead of say 500V, but it would still apply significantly more stress than a continuity test that only involves very low voltages.
A first test would be to connect only the hot of the circuit to the GFCI breaker output, but leaving the circuit neutral connected to the neutral bar. All loads should be disconnected. If the GFCI trips then that means there's leakage from the hot conductor to either the circuit neutral conductor or to ground.
If there's a trip during the first test, then a second test could be done to determine whether the leakage is going to neutral or to ground. For this test the circuit neutral would be connected to the GFCI load neutral terminal as is normally done. Then if the GFCI that was tripping on the first test now holds, that means the leakage is not from a ground fault but instead is caused by leakage between hot and neutral.
If tripping occurs in the tests above, then various parts of the circuit could be disconnected to isolate the problem area that causes it to trip.
Edit: I may have only assumed you meant to leave the pigtail disconnected. I read your post again and I don't see where you said that.