(a) Means of Identification. The means of identification for conductors #8AWG or larger shall be permitted to be by separate color coding, marking tape, tagging, or other approved means. Conductors of any size in cable assemblies may be suitably identified at all termination, connection and splice points. Conductor insulation in raceways shall contain continuous color pigment for circuit wire sizes # 10 AWG and smaller.
Phase Identification Colors for Branch Circuits shall be as follows:
(1) 120/240 Volt 3-Wire Single Phase Systems – “A” Phase Black, “B” Phase Red.
(2) 120/208 Volt 4-Wire 3-Phase Wye Systems – “A” Phase Black, “B” Phase Red, “C” Phase Blue.
(3) 120/240 Volt 3-Phase Delta Systems – “A” Phase Black, “B” (High Leg) Phase Purple, “C” Phase Red.
Information Note: New Construction or Complete Remodel of an Existing Building
(4) 120/240 Volt 3-Phase Delta Systems – “A” Phase Black, “B” Phase Red, “C” (High Leg) Phase Purple.
Information Note: Partial Remodel of an Existing Building – i.e. Replace Main Electrical Service where “C” Phase is Purple, & Re-Connect Existing Panels.
(5) 277/480 Volt 4-Wire 3-Phase Wye Systems – “A” Phase Brown, “B” Phase Orange, “C” Phase Yellow.
(6) Ungrounded conductors for other voltages shall be identified by different color coding, marking tape, tagging, or other approved means.
(7) Branch Circuit Conductors for switch legs may be of a different color than the Ungrounded Circuit Conductor when suitably identified at pull boxes, junction boxes and outlet boxes with marking tape, tagging or other equally effective means.
Exception No 1: In Multi-Family Dwelling Unit Buildings supplied by 120/208 Volt 4-Wire 3-Phase Systems, within Dwelling Units supplied by 120/208 Volt 3-Wire Single Phase Systems, Ungrounded Branch Circuit Conductor shall be permitted to be “A” Phase Black, “B” Phase Red.