In your previous thread you mentioned that the 11.33A load is for a sign and that other 120V loads could add up to a total of as much as 20A:
If you can fit four wires in the conduit for L1, L2, N, and EGC on a MWBC then you could put the 11.33A load on L1 and the other loads on L2.
If they were all #12s then the voltage drop you'd get on L1-N and L2-N vs. their currents would be:
Proportional Increase of EGC for VD
Hey all, question about some code lingo for you. My question is in regards to 250.122 (B) Increased Size in which, if we increased the size of ungrounded conductors for the purposes of voltage drop, we are required to increase the size of the EGC proportionately. I'm working with the 2014...
forums.mikeholt.com
If you can fit four wires in the conduit for L1, L2, N, and EGC on a MWBC then you could put the 11.33A load on L1 and the other loads on L2.
If they were all #12s then the voltage drop you'd get on L1-N and L2-N vs. their currents would be:
IL1 | IL2 | Itot = IL1+IL2 | IN = |IL1-IL2| | L1-N drop | L2-N drop |
---|---|---|---|---|---|
11.33A | 0A | 11.33A | 11.33A | 9.75V 8.13% | 0V |
11.33A | 8.67A | 20A | 2.66A | 6.02V 5.02% | 4.88V 4.07% |