Buck Boost Transformer
It's working now, and using 13.3%, I got the exact same answer.
Where did I go wrong in my formula? I'm off by a factor of 10.
I thought it was based on the boost voltage and load current.
The web site is a bit confusing. The recommended transformer is 2S46F, which, if you look it up in the catalog, is a 2KVA transformer.
The wattage figure shown, 19.47 KVA, is the total output power (apparent) of the boost circuit, all of which is ultimately derived from the input, but only a fraction of that power has to pass through the boost transformer itself.
I would say the 60a number. Remember, you only need to size the transformer for 60 x (240-208) = 60 x 32 = 1920 = 2 kVa.
The equipment is a Hot Tub. It has two, maybe three motors, and heaters.
Larry they have a separate calculator for motor loads. If you run the numbers there you get the 1920 VA or 2 KVA.
But Bill says the load will be motors and heaters so I don't know if you can use that calculator using only the boost voltage.
I think I would talk to someone at Eaton or Square D about the sizes.
With the 125% allowance, why would the heaters change the calculation?
I buy mine from Hammond; I typically use the square D Calc to size it, but the people at Hammond can also tell you what you need.
I’ve had to use quite a few on pool pump installs at houses with 208Y/120 services.
I got the transformer and hooked it up. The actual voltage that I measured was 213V so I got a little over 240V with the transformer.