- Placerville, CA, USA
- Retired PV System Designer
It's working now, and using 13.3%, I got the exact same answer.
Where did I go wrong in my formula? I'm off by a factor of 10.
I thought it was based on the boost voltage and load current.
The web site is a bit confusing. The recommended transformer is 2S46F, which, if you look it up in the catalog, is a 2KVA transformer.
The wattage figure shown, 19.47 KVA, is the total output power (apparent) of the boost circuit, all of which is ultimately derived from the input, but only a fraction of that power has to pass through the boost transformer itself.