puckman
Senior Member
- Location
- ridgewood, n.j.
does anyone know how to size a buck-boost transformer to get 3 phase 220 to 230 volt from 3phase 240 volt . the load is 75 amps. 240volt is to much voltage.
r u talking about going from 208 to 240 3 phase :-? am i missing something or ?puckman said:does anyone know how to size a buck-boost transformer to get 3 phase 220 to 230 volt from 3phase 240 volt . the load is 75 amps. 240volt is to much voltage.
Are you sure? 230v is the normal rating for equipment designed to operate on 240v.puckman said:240volt is to much voltage.
puckman said:3phase 208 - 230 at 70amp.
in that case go with a 30 kva 240v to 208v x 120v xfmer if u can get one in 30 kva our price cat. only gives 45, 75 112.5 and 150 kva call ur supplier he may be able to get a 30kva in these voltages. and what larry said i can't chew gum and type and think that fast.puckman said:3phase 208 - 230 at 70amp.
i think what u have is a unit that run on either 208 or 240 u would probly need to change some taps in the unit itself depending on the voltage avaliable also i belive the 187-253 is what the unit will run on before it is going to suffer as votltages vary Ex. 120v meter will somtimes read 123, 115 etc.puckman said:chris, no it is a roof top ac unit about 15 ton paper work says 208 - 230 volt. it also saids operating range 187 - 253 volts. unit was ordered before any contractors were hired. thanks to all
puckman said:chris, no it is a roof top ac unit about 15 ton paper work says 208 - 230 volt. it also saids operating range 187 - 253 volts. unit was ordered before any contractors were hired. thanks to all
You're good to go. No transformers needed, and there should be no taps to configure.puckman said:chris, no it is a roof top ac unit about 15 ton paper work says 208 - 230 volt. it also saids operating range 187 - 253 volts.
mdshunk said:Just make sure the tap on the 24 volt control transformer in the RTU is properly set.
puckman said:.... also saids operating range 187 - 253 volts...
That really depends. Yes, about 50% of the time I do have to terminate the stat connections, set the control transformer taps, and comfirm the rotation of the RTU. Other than that, it's the tin-knocker's baby. I only run the unit for a matter of seconds. I fully realize that in most areas, the electrician just gets power to the unit and never has to lay eyes on it again. I think I operate in an area where the HVAC guys are a little spoiled, but it's okay with me.chris kennedy said:I do change this tap but I feel that is the mechanical contractors responsibility on start up. You don't make up the Tstat terminations do you?