We have an application where a client has a piece of equipment that requires 480V 3ø. The service feeding the building is 120/208V. The same client occupies an adjacent building that has a 480V service. Based on 225.30(D) Different Characteristics. Additional feeders or branch circuits shall be permitted for different voltages, frequencies, or phases & 230.2(D) "Different Characteristics. Additional services shall be permitted for different voltages, frequencies, or phases..." I believe it is allowed to bring a separate 480V feeder to the building that only has the 120/208V service. Disconnect means would need to be per 225.32, identification would need to be per 225.37 and grounding per 250.32.
225.37 states Where a building or structure has any combination of feeders, branch circuits, or services passing through it or supplying it, a permanent plaque or directory shall be installed at each feeder and branch-circuit disconnect location denoting all other services, feeders, or branch circuits supplying that building or structure or passing through that building or structure and the area served by each.
and 230.2(E) states Where a building or structure is supplied by more than one service, or any combination of branch circuits, feeders, and services, a permanent plaque or directory shall be installed at each service disconnect location denoting all other services, feeders, and branch circuits supplying that building or structure and the area served by each. See 225.37.
Both of those statement imply that it is ok to have a building fed by a Service and a separate feeder. I was initially told that this wouldn't be allowed per NEC and would like to know if I'm applying 225.30(D) and 230.2(D) in the correct manner.
Thanks
225.37 states Where a building or structure has any combination of feeders, branch circuits, or services passing through it or supplying it, a permanent plaque or directory shall be installed at each feeder and branch-circuit disconnect location denoting all other services, feeders, or branch circuits supplying that building or structure or passing through that building or structure and the area served by each.
and 230.2(E) states Where a building or structure is supplied by more than one service, or any combination of branch circuits, feeders, and services, a permanent plaque or directory shall be installed at each service disconnect location denoting all other services, feeders, and branch circuits supplying that building or structure and the area served by each. See 225.37.
Both of those statement imply that it is ok to have a building fed by a Service and a separate feeder. I was initially told that this wouldn't be allowed per NEC and would like to know if I'm applying 225.30(D) and 230.2(D) in the correct manner.