Re: Bundled = Derated
If I bundle four 14/2 cables together then yes they get derated.
Four - two wire cables will be 8 current carrying conductors.
334.80 tells us NM can derated using the 90 C column of Table 310.16
Table 310.16 rates 14 AWG as 25 amps @ 90 C.
Table 310.15(B)(2)(a) shows that 8 current carrying conductors suffers an 70% ampacity reduction.
25 amps * .7 = 17.5 derated ampacity.
So my four 14/2 NMs through one hole will still be perfectly compliant.