If you have more than 30 current carring conductors bundled (ty-wrapped in lengths over 24") in a panel board, do you have to derate? As near I as I can tell in 312.8 you can use a panel board as a raceway, but that doesn't mean that it is classified as one. In article 366.22 (B), and article 376.22 reference 30 current carring conductors as a cut off to where you have to start derating, and article 310.15(B)(2) refrences the 24". I think it boils down to what a panel board is classified as. Dose any one have any thoughts?